Using the structural steel, or a grounding conductor that is not run with the phase conductors may not ensure that the ground fault current path is effective.
250.4(A)(5) Effective Ground-Fault Current Path. requires this path to be effective, therefore that would not be a proper method.
I know that the code permits a grounding conductor to be run to the nearest equipment grounding conductor, 250.130(C), but I say this is asking for trouble.