wireman,
There are breakers that have been tested and "classified" for use in panels made by other manufacturers. These classified breakers have been tested to the same standard as the UL "listed" breakers mase by the manufacturer of the panel. There is no code or safety violation in using classified breakers. These breakers are required to be supplied with a listing of panels that they are permitted to be used in.
Quote from UL Guide DIXF, "Circuit Breakers, Molded-case, Classified for Use in Specified Equipment".
Quote
This category covers Classified molded-case circuit breakers rated 15 to 50 A, 120/240 V maximum that have been investigated and found suitable for use in place of other Listed circuit breakers in specific Listed panelboards. The circuit breakers are Classified for use in specified panelboards in accordance with the details described on the circuit breaker or in the publication provided therewith.

[This message has been edited by resqcapt19 (edited 10-25-2003).]

[This message has been edited by resqcapt19 (edited 10-25-2003).]


Don(resqcapt19)