I think it would be very cost prohibive if not physically impossible to manufacture a GFCI that would disconnect the receptacle face as a result of mis-wiring.

The block diagram for a properly wired device is similar to:

[incoming power]->[Line terminal]->[GFCI sensing]->[power disconnect]->[receptacle face]->[load terminals]->[down stream devices]

On a miswired receptacle the power is applied to the "load" terminals and therefore directly to the receptacle face. To prevent this from happening a second set of disconnect contacts would be required after the receptacle face. A possible block diagram would then be:

[incoming power]->[load terminal]->[power disconnect]->[receptacle face]->[power disconnect]->[GFCI sensing]->[line terminals]->[down stream devices]

The all but failsafe solution: use GFCI breakers instead.