Any additional info here appreciated......

Quote
Dear Sirs or Madam;
I have a G3030B1100CU 100amp, 30 circuit panel.
The neutral (or grounded conductor)bar, when isolated from the grounding bar has only 24 terminations.
Is this panel listed to meet NEC 408.21 exception?
(below from the 2002 NEC)


408.21 Grounded Conductor Terminations.
Each grounded conductor shall terminate within the panelboard in an individual terminal that is not also used for another conductor.

Exception: Grounded conductors of circuits with parallel conductors shall be permitted to terminate in a single terminal if the terminal is identified for connection of more than one conductor.

Sincerley,
Steve