Can I use the 90ºC column if I'm using RHW-2/USE-2 for a commercial service? If so, then 100A Commercial service may use #2 Al RHW-2 Conductors?
My AHJ thinks so, but I thought we were limited to the 75ºC Column for services?
(Do to terminal temp ratings?)