Good Question. It doesn't seem to me that it would be required (not a bad idea though IMO) unless the rebar is somehow exposed somewhere and within 5 ft of the pool.

I say that because 680.26(B)(5) only mentions metal items (not part of pool) must be bonded within 5 ft unless "separated by a permanent barrier" Would you agree that concrete would be considered a permanent barrier?

Bill


Bill