Actually, I'm a tad [Linked Image] myself here.
From the 02';
680.43(a)(2)
all receptacles, 125V, 30A or less within 10' shall be GFI
680.44(a)
basically states that no GFCI protection is required when provided with the unit.
680.43 comply's with section 1 & 2 of 680, unless modified.
680.22(a)(5) asks for GFI protection within 20' of pools

I think 44a modifies 680, and insinuates a dedicated (single) receptacle.

Others may clarify this better.

[This message has been edited by sparky (edited 11-04-2001).]