Bill,
Before the 2002 code came out I would have said that the receptacles in an appliance garage had to have GFCI protection, but the new code tells us that any receptacles in appliance garages can't be counted as the required countertop receptacles. If they can't be counted as a required counter receptacle, then they must not be intended to serve the countertop, and if the don't serve the countertop, GFCI protection is not required. I would expect that this will be changed in the '05 code to require GFCI protection for the appliance garage receptacles.
Don(resqcapt19)


Don(resqcapt19)