motor-T,
there are plenty of individuals living 'off grid' using a stand alone System , as it is still a dwelling, the 125v ( debatable code vernacular) is to be wired compliant to 210-12, et all..
Where Trace & Hart may have a 30-50 step 'wave', others may not, and disclaimers for 'sensitive' electronic equipment follow suit....thus my concern....
I do not see mention of a GFI protection level on the instructions per se', but i do see much to insinuate GFI configuration @ Zan's site , i.e.-current x-formers w/logic,
oh, note on the inst. the megger warning, then think 30 yrs of spikes from now... [Linked Image]
To further purse the 'GFI' similarity read here
in response to 'parrallel' arc's...
electronic circuits can detect it easily and trip the breaker in a fraction of a second.
in response to 'series' arc's...
Since the peak current is never greater than the steady-state load current, series arcing is much more difficult to detect than parallel arcing.
note parrallel seems no problem, series is graciously avoided....
Zlan DE Circuit Breaker, hopes to sell his patented circuit breaker to an established manufacturer of electrical equipment for a price only slightly higher than breakers on today’s market. He also patented a testing device which can assess the safety of electrical circuits and can pinpoint any deficiencies. These inventions are not on the market yet, but when they are, they should be a major breakthough in electric safety.
I for one, am still waiting........ [Linked Image]
[This message has been edited by sparky (edited 02-28-2002).]