Steve,
Send me some numbers and I'll do a Volt-Loss calc. for you.
Need one way length[s], total load current [or Volt-Amps] per circuit, system voltage [nominal rating], voltage at the subpanel feeding these lighting circuits [under a high load would be best], type of conduit [magnetic or non-magnetic], power factor [list lamp wattage, then it's noted RLA and I'll figure PF].
If you want, I'll do one for the connected load, and one for max. circuit load @ 0.8 for LCL.
The 17 watt CFL [compact Fluorescent] must have had a typo' for the RLA. 1.4 Amps would put the line Volt-Amps at 168 VA, resulting in a PF of less than 10% [anything less than 50% is going to get the utility people raging mad!!].
Take an ampere reading yourself to get an idea of RLA.
Scott SET.