For installing stress cones on 15kv uni-shield cable:
For those of you that have worked with uni-shield, you know it has the shield wires under the outer insulation that run parallel along the length of the cable. The stress cone kits require you to strip that outer insulation back for a specific length for the stress cone. I always mark that measurement with a regular hose clamp lightly tightened on the cable. I then lightly score the outer insulation at the edge of the clamp, use my heat gun to heat the cable, and soften the insulation. Then I take my linemans pliers and grab each shield wire and pull it back toward the clamp. It cuts right through the insulation. Then I peel the sections of insulation back like peeling a banana, and it pulls off at the score mark I made next to the hose clamp.