I found the problem today on the wrong 3ph voltage readings. The customer had some so-called electricians out to do some work previously and they shorted something and blew one of the 3 legs (Phase A) at the meter where the panel was fed from, and they could'nt figure it out so they tied the circuits that were off to breakers on the other working phases just to get it working.
The reason I was getting reading on all 3 phases is it was being backfed through some load. Hard to believe someone could do this and then cover it up and leave it because they couldn't figure it out. It was a new Meineke Muffler business and wasn't open yet so the customer would'nt have noticed more problems until later.