Quote
A properly sized and connected Grounding Electrode Conductor

I have to disagree with that.

The only electrode that might keep a lost neutral from causing voltage imbalance would be a metal water pipe that is electrically continuous with your neighbors neutral.

If that is the case you have only postponed the problem till someone separates the pipe and gets a shock while doing so.

The other types electrodes, rods, plates, concrete encased etc. will do very little to keep the voltage balanced with a lost neutral.

Bob


Bob Badger
Construction & Maintenance Electrician
Massachusetts