Suggested components may be:

www.fciconnect.com/pdffiles/brochures/Section_C_2003MC-Compression.pdf

TYPE YE-P “HYPLUG” FOR COPPER CONDUCTOR page 115 are likely not suitable for QO-breaker terminals.

TYPE YH H-TAP COPPER “CRIMPIT” page 107 with ~4AWG-stranded cable “pigtail”/jumper may permit a compact reducing splice.

Hydraulic tooling required for either.

N.B., physically larger “industrial E/F-frame” 15-150 ampere molded-case circuit breakers are routinely available with terminals for 1/0AWG conductors.