I also do the "Hot" test to verify the meter [tester] works, then open the circuit and re-test.
LOTO the heck out of any and all disconnecting means, even pull fuses out of switches if there's any possible jokers
Got hit once from 277 VAC, and it hurt plus shook me up quite bad! Glad to say only hit once [also glad to be alive today to say I got hit once!]
Canadian Sparky,
As to your question about the 347Y/600 Wye system, you guys in the "Real Great White North" [the one that Bob and Doug are from, plus the one north of Washington, Idaho, North Dakota, Wisconsin, Etc.] are the only North American country with it.
Down here, we have a 3 phase 3 wire Delta, which is 600 VAC, but the only low voltage [under 1 KV] 4 wire Wye systems are 208Y/120 and 480Y/277.
Depending on the size - in square feet - of a commercial / industrial structure, the system voltage from the utility company could be 208Y/120, 480Y/277 and upto 4160Y/2400. All this to get the required KVA into the building.
Of course, normal office lighting would be dangerous at 2400 VAC - switches would be killing people left and right!, so the better lighting voltage for large structures is 277 VAC.
Scott SET