What size wire are you going to be pulling? It sounds like you are planning on entering the panel (loadcenter) opposite the branch circuit breaker area. If that is the case there isn’t enough wire bending room for large wire. You should either offset the conduit to enter the top or bottom of the side or install a pull can beside the panel to offset the wire into the correct area of the panel.

Edited to add NEC reference. See 408.35