I assume arial messanger cable to the building? Coming from a pole? Pole mount meter/disco not a common occurance where I'm at, but with grounds, and nuetral bond at both, I don't see a problem. In fact doing it otherwise may be a (local)violation. I would see the pole as a structure, and the house a seperate structure.

Covered in 250.32, provides two methods. One with both having a seperate ground, 4 wire no neutral bond at the house. And the second with both having a seperate ground, 3 wire with neutral bond at the house.

The second being more prefferable, due to possible damage to an arial cable. If neutral loss occurred, you have an over-voltage fire hazard. Opposite phase loads would re-connect at the damaged neutral!

Unless this was underground in steel conduit... The first method! Then you have parralel neutral path, a different story.