All we do is telecom and data. Here is what you need to do:
1) Data jacks are orange, CAT5 or better. ALWAYS USE THE 568B WIRING SCHEME. I recommend Leviton #41108-RO5. These are "keystone" jacks that snap into a plate. Single gang plates are available with up to six ports.(Six jacks). We usually use the 3 port, #41080-3*P. (replace * with W for white, I for ivory). Use #41084-B*B to blank up any unused ports.
2) The voice jacks are CAT3. These are 6 pin jacks #41106-R*6. Only punch down the wh/bl and the wh/or pairs. The other two pairs are spares. We always make the voice jacks the same color as the plate.
3) At the other end, terminate the voice runs on a 66 block. (Leviton #40066-M25)(Sorry Sparky, I've never seen that junk you are using.) This is a split 50 pair block which means that you can put 6 four pair cables on each side. Always install a 66 block on a 89D standoff bracket. (Leviton # 40089-D) YOU WILL HAVE TO KNOW THE COLOR CODE!! If a telcom vendor is going to install a system DO NOT DO ANYTHING WITH THE VOICE CABLES. Don't punch them down, leave them long enough at least to reach the floor. Cut them all to the same length and coil them up together into one neat coil. Don't waste your time marking or tagging the runs. We will tone them out as we terminate them.
4) The data runs get terminated on a patch panel. For 13 runs you will need a 16 port #59484-U16. This is a 1 space by 19" rack panel. Use a hinged wall bracket to mount it to the wall. REMEMBER TO USE THE 568B SCHEME when you punch your cables down.
5) You will need a punch down tool with a 66 blade for the 66 blocks and a 110 blade for the jacks and patch panel.
6) NEVER, repeat NEVER even think about certifying the data runs (voice runs don't get certified) unless you absolutely have to. CAT5 cable must be run absolutely without kinks, tight bends or crushes and must be terminated flawlessly. If any of this is not met it will not certify. This doesn't mean it won't work or anyone will notice a problem (unless you really butchered it), it just won't certify and you will have to replace the run. No matter how much experience you have, or how many helpers, you always will have kinks in this stuff. Hopefully you straighten them out but the run can still can fail certification.
7) If you are using plenum rated cable, consider using CAT3 for voice. This is less than half the price of CAT5.