Matt,
If everything in the circuit including the equipment is listed for use at 75°C, then yes we could use the 75°C ampacity forom the table.

In the long term, it would never pay to run a 90°C conductor at its full ampacity between junction boxes, do to the increase in energy costs to heat that wire to 90°C.
Don(resqcapt19)