2002 NEC 210.4(B) does not require a common trip breaker, this was pointed out to me on this forum in another post.

You can use a common trip breaker or you can use a approved handle ties with single pole breakers.

2002 NEC
Quote

210.4 Multiwire Branch Circuits.

(B) Dwelling Units.

In dwelling units, a multiwire branch circuit supplying more than one device or equipment on the same yoke shall be provided with a means to disconnect simultaneously all ungrounded conductors at the panelboard where the branch circuit originated.

2002 NEC Handbook commentary on this.
Quote
The simultaneous disconnection can be achieved by a 2-pole circuit breaker or by two single-pole circuit breakers with an approved handle tie,

[This message has been edited by iwire (edited 06-13-2003).]


Bob Badger
Construction & Maintenance Electrician
Massachusetts