The balanced power system is only permitted in commerical or industrial occupancies. See 647.3(1).
The equipment grounding conductor is required by 300.3(B) to be in the same raceway or cable as the power conductors. On high amperage circuits a remote equipment grounding conductor will have a high impedance because of the inductive reactance.
Don


Don(resqcapt19)