A 15 amp breaker can be loaded up to 15 amps for Non-continuous loads.

For continuous loads no more then 12 amps (80%)

The code does not use 80% as the terminology they have you calculate a continuous load circuit at 125%, but the result is the same


Bob Badger
Construction & Maintenance Electrician
Massachusetts