Recently had occasion to address this situation again, and I now believe that the conclusion from the original discussion was incorrect. While the requirements of Article 770.48(A) haven’t changed, in the 2017 NEC a paragraph was added to 770.48(A) to clarify those requirements. In particular, it states that to extend the point of entrance, the cable must be "continuously" enclosed in IMC or RMC. That would seem rule out such things as pull boxes which would ordinarily be allowed in a raceway system. Had I looked at the 2017 NEC (instead of 2014) when I originally asked the question, well..……..I wouldn’t have needed to ask.

I know that no one has been losing sleep over this scenario, but I just wanted to set the record straight (at least as I now believe it to be).