As a general rule you don't use the "definition" section to describe methods. That is just defining terms. Go down to section II in article 770 to read more about fiber entering buildings. (starting at 770.47)
If you look at raceways in Chapter 3 of the code you will see that boxes and conduit bodies are considered to be part of the raceway system if they are installed in the correct manner so that part of your question is "yes" they are allowed in that system.