Added thought: The equipment grounding conductor in each cable must be full sized based on Table 250.122.

(d) Except as provided in 250.122(F)(2)(b) for raceway
or cable tray installations, the equipment grounding conductor
in each multiconductor cable shall be sized in accordance with
250.122 based on the overcurrent protective device for the
feeder or branch circuit.


George Little