I think your guidance is in 250.122(F)(2) and it looks OK to me as long as they get grouped on a bus or common connected pair of lugs on each end.

Quote
(2) Multiconductor Cables.
(a) If multiconductor cables are installed in parallel, the
equipment grounding conductor(s) in each cable shall be
connected in parallel.


Greg Fretwell