What kind of computers? Do they need 3P?
If you are just talking about 1P computers, like PCs, don't forget the triplin harmonic problem when you are connecting to 3P wye. The shared neutral in the 3P feeder should be up to 2x the size of ungrounded conductors. Once you get to the single phase (2 wire) branch circuits it is not a problem


Greg Fretwell