"A 20-a circuit is a code violation when the appliance it is designed for draws less than 16 amps. Add the required additional overcurrent protection, and it's no longer a '20-a' circuit."

&&&&

This interpretation reads backwards for me. I've always taken the position that a 20A branch circuit is suitable precisely when the utilization will be 80% and below.

UL listed appliances come with overload appropriate cords.

Small appliances also come with internal overload protection -- either inherent or as a component -- like a Klixon. (Common as dust inside appliances across the land, many flavors.)

Over current protection is to exist back at the panel for said 20A branch circuits.


&&&

My 2 cents on vehicle collision damaged raceways is that there are no raceways that can 'take' vehicle collisions.

Even RMC/ GRC would be crushed by a lift truck.

Fork lifts are the reason bollards were invented, IMHO.