Originally Posted by frank
The disco is fused at 50a and the motor FLA is 40a
The issues I have with it are
-the lack of O/L protection


In the US overloads are sized to 1.15 the motor's load.

40 amps translate to 46 amps if you multiply it. The next standard fuse size is 50 amps.



Last edited by electure; 05/05/14 05:41 PM. Reason: I noticed Frank's in Canada