What Joe is saying is "selective coordination" in basic terms. If you have GF on the 'Main', and on panels further downstream, the downstream panels should be at a lower setting then the 'Main'.

It sounds like the facility you were in only has GF at the 'Main', which is fairly common.

Testing and adjustments to GF trip settings and times should be based on the factory specs, or engineering studies.


John