Just ran into this a couple weeks ago. 250.34 does not require a grounding electrode if the load is fed from receptacles mounted on the generator. How about if the load is cord is fed from the bolted lugs on the generator?
Bolted lugs do not fit the definition of a receptacle so
technically would a ground rod would be required?