Nevin. you need to put in the 60 amp fuses per code.sizing motors,wiring, overloads, breakers or fuses is a gray area for a lot of electricians,even me years ago.but it not that hard.take the hp of the motor and check the code book 430-150 3 phase go down to 25 hp.now over to the voltage 460 it says 34 amps.now go to 430-152 time delay fuses it says 175% so now 34 x 175 = 59.5 amps.code 430-52 allows you to go up to the next standard size fuse or breaker look in 240-6. put in the 60 amp fuses [Linked Image]
an here one to think about. if you were to use one time fuses 34x300%=102 amps,you would go up to a 110 fuse and all on that # 8 wire.