Nevin, What voltage is your compressor running at? FRS-R's are rated for 250 Volts. If someone accidentally grabbed the wrong fuses out of the drawer, (I've seen it happen) and installed them into a 480 Volt circuit. The results from the insulation breakdown would be consistent with the damage you describe.