Originally Posted by ayrton
350kcmil THHN 90 deg C is 350amps x 8 conductors is 2800 amps. Service is 2500


You can not use the 90 degree column unless the lugs AND equipment are rated 90 degrees and unless I'm mistaken there's no service equipment or transformers rated as such.

You can use the 90 degree column for derating though.