Alas, with synchronised AC systems it just isn't that simple! (as it would be with DC) Just having a higher voltage would cause the inverter to export reactive power (VAr) but not real power (kW). To export real power it must create a sinewave which is very slighly ahead of the sinewave from the grid....ie its trying to pull the grid faster, this causes it to export power.