Grover:
220.61 (from '11)
"(C) Prohibited Reductions. There shall be no reduction of
the neutral or grounded conductor capacity applied to the
amount in 220.61(C)(1), or portion of the amount in (C)(2),
from that determined by the basic calculation:
(1) Any portion of a 3-wire circuit consisting of 2 ungrounded
conductors and the neutral conductor of a
4-wire, 3-phase, wye-connected system
(2) That portion consisting of nonlinear loads supplied
from a 4-wire, wye-connected, 3-phase system
Informational Note No. 1: See Examples D1(a), D1(b),
D2(b), D4(a), and D5(a) in Informative Annex D.
Informational Note No. 2: A 3-phase, 4-wire, wye-connected
power system used to supply power to nonlinear loads may
necessitate that the power system design allow for the possibility
of high harmonic neutral-conductor currents."
In addition to the above, a local POCO does NOT allow reduced neutrals for comm/ind. services that have a neutral.