My neighbor is getting a permanent above ground pool and yours truly gets to run the power. No heater. The only thing it needs is a generic 120V GFI for the pump/filter unit (which draws 7 amps, has a 3' cord and straight blade plug). The pool guy wants a post with the GFI 5' from the pool so he doesn't have to run longer pipes. I'm telling him no way, a disconnect can be 5' but if there is a recep involved for the the pump/filter (with a straight blade plug) the recep must be 10' (680-22A1). He says "That's what we always do". To which I responded "You're always wrong". (We're on 2008 here). Am I missing something or is he full of it?