Nope- I don't see any way out of this one. You definitely have a situation where you are feeding the garage with two sources of power. You have the feeder and also a branch circuit. Clear violation of 225.30. The only out of it is to re-wire the three way circuit so that the power originates out of the panel in the garage.

Harold I understood that the panel in the garage is fed from the house and has a main disconnect in the panel, and that additionally there is a branch circuit originating from the house for lighting on/in the detached garage, with a three way switch located in the garage. The hazard could be that a person could turn off the main in the sub panel and then go work on the three way switch. Clear possibility. 225.30 is the code reference. Red Sticker under my inspection.


George Little