Short answer: No

Your not being clear on the term structure. It's not possible to have a circuit originate at a detached structure. I'm assuming the detached structure is the garage and the house is the other structure. One could argue that the house is detached from the garage and vice versa. Assuming the house is the main structure and it has the panel in it, than the other structure could be a detached structure maybe a shed or garage and it could have a 3-way switch in it that could qualify as it's disconnect.


NEC 225.36