That is quite a nice newsletter!
As for bonding CSST .... we've discussed this here several times, and there's been much hand-wringing over the lack of approved clamp for attachment to either the CSST itself, or the fittings at the end of the CSST. As the newsletter illustrates, this concern is based on a misunderstanding of what is meant when the instructions ask you 'bond' the CSST.
No, you're NOT trying to attach a wire directly to the CSST at both ends, and you're NOT being asked to run a wire along the side of the tubing.
Instead, you're being asked to simply connect a wire to the gas supply pipe. Make a 'gas bond' n a manner similar to the 'water bond' we've been doing for a century.
The one difference is that you're allowed to land the wire on the external bonding strip that we're now expected to have at each service.