Canadian Code is pretty clear...

10-906
(7)In the case of metallically enclosed systems where the grounding path is provided by the metal enclosure,
a bonding jumper shall be installed to bond the grounding terminal of the receptacle to the enclosure.

(8) Notwithstanding Subrules (6) and (7), the bonding jumper, in the case of receptacles having grounding
terminals isolated from the mounting strap required for special equipment, shall be permitted to be
extended directly back to the distribution panel.