Greg,

"The problem is most solid state switches want to disconnect on the zero crossing. L/L on a wye is never zero so they always open under a load."

That statement has been rolling around in my head and bugging me for a couple of days, so I finally looked it up.

L/L loads do have zero crossings and they do happen at the same frequency as L/N loads. They are just phase shifted by 30 degrees.

L/L loads obviously are at higher voltages than L/N loads on the same system. That may be why the relays might have a higher failure rate when used on L/L loads versus L/N loads.