Various relay and industrial controls manufactures offer a wide assortment of noise suppression components. For DC coils, a 1N4003 diode across the coil will suppress most inductive kicks. For AC coils, a snubber made up of a resistor and capacitor will provide a shunt path to limit the inductive kick.

Seperation and proper shielding is the key to reduce cross talk issues. For sensors with high impedance inputs, twisted shielded pairs are usually the answer. Twisted pairs ensures any noise picked up by the wiring is present equally on both wires. Since the input is typically looking at the difference between the two wires, the same noise on both wires is ignored.

Shielding is a bit trickier. If you are shielding against low frequency noise (DC up to 50-100 KHz) connecting one end of the shield to frame or earth will usually do it. Typically the location where most of the cables come together is where you ground.

If you are shielding against Radio Frequency interference, ground often and everywhere you penetrate a shielded bulkhead. Don't mix sensitive signals with unshielded signal conductors when possible. The unshielded conductors can radiate the noise back into the sensitive signals.

If you are dealing with high current wiring (100's Amps) being parallel with the sensitive signal wiring, magnetic shielding may be of concern. Running the sensitive wiring in steel conduit is usually the cure.

If all the controls are low impedance items like relays and indicator lamps, electrical noise will probably not be an issue. Susceptable signals vould be things like millivolt signals for temperature, position, or the millivolt voltages of current shunts. Shielded cables and separate conduit runs would take care of 99% of those issues.

If all the sensitive instrumentation is mounted in a grounded conductive enclosure, I would not expect for there to be any issues.

LarryC