Harold

I have seen that too but then the question becomes "is that down rod a raceway or just part of the fixture"?
It is not really part of the fixed building wire or a chapter 3 wiring method. It is "fixture wire".

310.15 says
Quote
Where the wiring method is conduit, tubing, Type AC cable, Type MC cable, Type MI cable, nonmetallic-sheathed cable, or other cables, a box or conduit body shall be installed at each conductor splice point, outlet point, switch point, junction point, termination point, or pull point, unless otherwise permitted in 300.15(A) through (M).


Greg Fretwell