There are metal halide open glass type hanging fixtures. The contractor wired them with rubber cord, outlet above fixture, and they are 480V. Are the fixtures allowed to be fed with rubber cord? I thought the flexible cord would need to be rated at 90C? I don't like the idea of 480V for a plug in style High Bay fixture. There were some fixtures that had the receptacle 2 feet away. We turned that down and said the outlet has to be directly above the fixture.
Thoughts on 90C rubber cord?