"But seems to me theres a lot of inspectors & qualified people that are on this site that might be reviewing prints such as theses"

FWIW, I have not had to review anything as you describe.

Fire Pumps (and I have reviewed many) have individual POCO service, none have included a genset.

"So I take then that they take it for granted what ever the designer puts on the prints well pass????"

Yes, it will 'pass', as long as it is compliant with the adopted NEC. On average, for Plan Review, 3 to 5 rejection letters are generated every week. Design professionals are, like you and I, human...and we all make mistakes.

"When this comes up for Plan Review Where well the Plan Reviewer go for the answer???"

The 2008 NEC, for the Electrical design (edit to add "CODE COMPLIANCE"), and pass plans on to the Fire Subcode Official for his NFPA Code compliance review & comments.(edit to add hydrostatic design compliance)