GregTaylor, even if I apply your interpretation, how on earth would an inspector catch it?

I ask this because the two SABC's can be served by a multi-wire circuit (share the neutral). 2008 code rules would then require the use of a 2-pole breaker - making it impossible to turn off just one side.

Breaker -> 240 receptacle -> first 120v circuit
. . . . . . . . . . . . . -> second 120v circuit

Assuming the 240v receptacle is serving the kitchen area, where's the code issue?

I don't like the plan, but I can't find the code to cite.

Noderaser, you nailed it: in those antique buildings, every tenant has their own transformers, or has had to obtain special equipment.

Why don't they upgrade the buildings? That often goes back to the original manner of construction. One of the buildings I referred to is known as the 'first' skyscraper - a massive, solid masonry 10 story building. You don't easily change such things.