We just wire the doors through the push button switch at the pull station and use notifer monitor modules for the system.I have also added extra switches to the pull station if needed.What system do you have?
The mag locks must release imediately by law as the system may take up to 15 seconds to release the doors causing the occupants to look for another escape route.The mag locks cant be soly wired into the system for this reason and must be hard wired directly to the doors as well.So the hard wiring goes through the switch and is redundant as the mag locks are also wired through the fire relay. We then have tyco come in and certify it.I can get you part #s if you like hope that makes sence
cheers