Only if it is 120v 15 or 20a and this is not limited to bedrooms. (NEC, I am not sure what New Jersey says)
As I read it you would not need AFCIs in basements and garages unless they were converted to one of the uses in 210.12(B). I guess the open question is what is the trigger that changes a basement (or garage) to a recreation room? We had the same issue, going the other way with GFCIs for all of the 120v 15/20 receptacles. In any case you would need one or the other.


Greg Fretwell