so would adding a few inches of newer 90C wire in the box bettween the K&T and fixture wire(s) make this compliant mikesh?
~S~
For my answer is no it is not compliant at all due the oringal T&K do not have grounding conductor there at all and I did recall the NEC stated that you can not extend the groundless conductors.
Merci,Marc